2017-10-16 8:14 AM
Working with the STM32L052C8 using the HAL commands.
I'm using the 'HAL_Delay()' command which is meant to be a delay in ms but I'm measuring HAL_Delay(1); to be 15ms. Checked with the data sheet and it says to have the Cortex System Timer at 4MHz which I have got by using Cubemx. Any ideas would be greatly appreciated, Thanks.2017-10-16 11:12 AM
if it's based on 1ms systick, the actual delay is anywhere between 0 and 1ms; with argument (5) it would be between 4 and 5ms etc.
Checked with the data sheet and it says to have the Cortex System Timer at 4MHz
Don't understand, give pointers.
JW
2017-10-17 1:12 AM
In the reference manual for the STM32L0 #12.2 it says about the Systick clock to be set to 4MHz, which is the Cortex System Timer in Cubemx. 2 images shown below.
So I set this to 4MHz and measured the HAL_Delay(1); but it measured as 15ms on a scope, instead of 1ms.
Thanks,
Richard
2017-10-17 3:22 AM
I think there is a misunderstanding on your side.
The ref manual means here that this SysTick calibration value (4000) is calibrated for a system clock of 4MHz.
4MHz / 4000 = 1kHz => 1ms
SysTick itself is just a 24-bit counter that works on the core clock.
If the SysTick is not what you expect, the core clock is most probably not what you think.
Don't know (or care) what Cube does here, sorry.
2017-10-17 3:30 AM
The systick calibration value is content of a read-only register, STK_CALIB, and is just a hint (btw. if it's really 4000
https://community.st.com/0D50X00009XkaB4SAJ
, but I am not surprised and it is really of no importance). You can set the systick to any division rate in STK_RVR. Read chapter 4.4. of PM0Cube surely has some mechanism to set this, but I don't Cube. Cube has some documentation so you can try to find it there. Cube is open source so you can look it up. And you can always look in the debugger at the actual STK_RVR setting.
But I repeat, with a 1ms granularity primary source, 1-tick loopdelay may last anywhere between 0 and 1ms. Try a longer one and divide the result for more precision.
JW
2017-10-17 3:35 AM
The ref manual means here that this SysTick calibration value (4000) is calibrated for a system clock of 4MHz.
4MHz / 4000 = 1kHz => 1ms
That would be true, wouldn't systick count from (reload-value -1), but it does not.
When enabled, the timer counts down from the reload value to zero, reloads (wraps to) the
value in the SYST_RVR on the next clock cycle, then decrements on subsequent clockcycles.To generate a multi-shot timer with a period of N processor clock cycles, use a RELOAD
value of N-1. For example, if the SysTick interrupt is required every 100 clock pulses, setRELOAD to 99.I ranted already, see link in my previous post.
JW
2017-10-17 4:22 AM
That would be true, wouldn't systick count from (reload-value -1), but it does not.
You are correct.
But with 15ms instead of 1ms, there is something else substantially wrong.
Cube surely has some mechanism to set this, but I don't Cube.
As said, +1.
I used to have such large SysTick 'deviations' when the clock setup was incorrect.
Which should be easy to find.